A fixed storage type water heater of 120 gallons or less shall be considered a continuous load, with branch circuit conductors having an ampacity of what percentage of the nameplate current rating?

Prepare for the NYC DOB Master Electrician Exam with tailored quiz questions. Boost your confidence by exploring comprehensive hints and explanations to excel on your electrician test.

For a fixed storage type water heater with a capacity of 120 gallons or less, it is important to apply the correct ampacity rules as specified in the National Electrical Code (NEC) and building codes. The code states that when determining the ampacity of branch circuit conductors for continuous loads, which include water heaters that operate for three hours or more, the conductors must be sized based on 125% of the nameplate current rating of the equipment.

The reason for this is to ensure that the conductors can safely handle the continuous current without overheating. Continuous loads can create a situation where the conductors carry current beyond their rated capacity, so applying the 125% rule allows for additional headroom. By sizing the conductors to 125% of the nameplate current, you help prevent thermal overload and maintain safety in electrical installations.

This specific requirement is important for compliance with electrical codes aimed at ensuring the safe operation of electrical devices. Therefore, identifying that the correct ampacity is indeed based on 125% reinforces best practices related to electrical safety and proper installation procedures.

Subscribe

Get the latest from Examzify

You can unsubscribe at any time. Read our privacy policy